[技术互助] A Tip on changing 3 phase AC motor rotation

[复制链接]
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 11:27 | 显示全部楼层 |阅读模式
老杨团队,追求完美;客户至上,服务到位!
本帖最后由 td456 于 2010-4-14 12:28 编辑 1 @9 [! _' j6 v: z

/ N& X' e4 p7 G8 n) I5 `We all know that if you want to change the rotation of a three  phase AC motor.
! |) q" b. i5 F; |/ gJust swap any of the two phase leads.4 s# ~/ \+ a# W0 h7 b5 }  c, G* `2 F
But for VFD application you need to do the swap after the inverter.
3 v6 P! t( |( }/ M2 D" `If you swap the leads before the inverter, it will not work.
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 18:18 | 显示全部楼层
go go go
鲜花(0) 鸡蛋(0)
发表于 2010-4-19 14:38 | 显示全部楼层
Yes, Good point.- `# e6 Z1 D& m/ V

3 p! W$ F! v+ ]; ], VAs the principal of the VFD works, bascially from AC to DC, then DC to AC.
& ~- Y" \9 G9 q7 L/ H5 @$ k; k9 j# s
The phase rotation of the output of the VFD connecting to the motor is based on the sequence "open" or "close" controlled by the inverter pre-set inside; any changes to the phase rotation of the feeder will not affect the DC rotation, as DC is NO phase at all.
& i: a3 l* i- X1 O
! U. I* ?, V2 Z0 VThe only thing you can change the rotation of the motor is the output side of the VFD, NOT the input of the VFD.