[技术互助] Any input on Cutler-Hammer Starter?

[复制链接]
鲜花(0) 鸡蛋(0)
发表于 2010-3-26 12:56 | 显示全部楼层 |阅读模式
老杨团队,追求完美;客户至上,服务到位!
本帖最后由 td456 于 2010-3-26 14:14 编辑 : C1 Y3 Q$ X" W% R! A7 ?
7 ?$ g9 j0 h" I6 J% x  o+ g
Two  cutler –hammer advantage  starters are  doing the same thing:4 U( S$ v1 V2 A( G1 L
After start 2-3 times, they will quit working, if you toggle the  start and stop buttons on DCS screen  , you will get another 2-3 running before they quit working again.
, m2 `( V4 F, h: z/ ~0 f- NIt is a cycle.
+ ]' L3 {% r# W4 i
. u3 t* y3 z) Q, E' N5 w% E/ ~We isolate the network control and use the local start and stop only, the problem remains.
. k0 }2 v6 y1 M% h  OSwap one of the defective buckets with a good one, the new bucket works fine.
/ W* [6 x5 S# Q7 cThe problem should be inside the bucket.( W  E* y9 `0 T

( e' `! h, K1 O2 ^1 X. zWhen the problem happened, we observed that  the contactor has a pulling action but will not seal.
0 ^8 u2 Y' p# q$ T; |Use a terminating screw divers to push in the contactor, it will not seal either.
# j# n. I- Q/ o* KConfirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we  bought two new control circuit boards and replaced the old ones, the problem is still the same." G8 k# X8 M+ F3 ~0 g

- ]: W' i( t) V* ~The next thing we can think of  is the coil, we took the coil out to have a close look.- U% B9 c1 }' T( |  ~) |6 c/ @
They  have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered  the connection and tried again.
& _4 P% X# {5 D$ W' `( \3 H It is getting better  this time, we have 7-8 times of running before it quit working. 3 E  w! v5 ]4 q: Z) U& C

1 Y8 h% K7 r/ t; z, ^The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them.
' ]8 a( P" y: }' }# W! X6 I# u  ]& h, E% V  Y' \8 U0 {
Do you guys have any input on this issue?
鲜花(1) 鸡蛋(0)
发表于 2010-3-26 17:07 | 显示全部楼层
有时候主接触点太脏,也会造成启动器无法正常工作
鲜花(0) 鸡蛋(0)
发表于 2010-3-26 17:37 | 显示全部楼层
本帖最后由 贾电工 于 2010-3-26 18:38 编辑
. P  L$ d/ J2 u: g7 ?' R* t+ \& ]+ ]: R, K) g
中国人在这里最好说中国话!说英语或想学英语请人到洋人论坛!
鲜花(7) 鸡蛋(0)
发表于 2010-3-26 17:42 | 显示全部楼层
老杨团队 追求完美
Don't know cutler –hammer advantage  starters very well, but had been worked on AB switch gears for a little while, which has two different coils, one to pull the vacum bottles up which employs larger current, another one uses less current to hold the connection---if the second coil fails, it won't be able to seal the connection.
% ]( R; j1 H& [( ~" _Since your cutler -hammer works couple times,  I guess 侠客行 is right, or the sealing connection is just worn out.
理袁律师事务所
鲜花(0) 鸡蛋(0)
 楼主| 发表于 2010-3-26 17:55 | 显示全部楼层
2# 侠客行
6 l# @# B/ G* e( L也想到这一点,不过这是新装的设备。
  o+ |/ d& }, A! @- Z检查过触点没问题。