" x, I" h: I7 ZTwo cutler –hammer advantage starters are doing the same thing:4 a; @, m: m* r6 Z3 w3 _
After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again.
. j: y9 T# G! A) D& o1 GIt is a cycle.
3 u% i1 W1 X2 L. w7 I0 j- O: y6 j
4 k |( }+ H" }4 BWe isolate the network control and use the local start and stop only, the problem remains.
: d) { t% `( ]Swap one of the defective buckets with a good one, the new bucket works fine.' U; @0 k: q" ^ H/ @- _
The problem should be inside the bucket.; \7 h9 z& _5 k9 h0 D
$ Z' n8 q& i' @& |When the problem happened, we observed that the contactor has a pulling action but will not seal.4 p% g1 W( e0 _0 D+ @& P
Use a terminating screw divers to push in the contactor, it will not seal either.
7 t& b7 U4 g& s+ q a2 u. \Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.! Z2 V* T) d9 a" o: \2 h
3 q5 a! g S- t
The next thing we can think of is the coil, we took the coil out to have a close look.# H( x0 M4 b6 u+ d/ X
They have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.
. r$ q6 V% D4 I It is getting better this time, we have 7-8 times of running before it quit working. / ~( ~- T: p% O0 s, u
2 [ L! w. o0 P: v0 \# wThe coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them. 3 V! g* A. i6 R
- a4 r [. c7 T( cDo you guys have any input on this issue? |
|